Timers

ANVER

Home Forums Timers

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #21987
    admin
    Participant

    Shaun;You need a Normally Open (Normally Passing)(Time Off Delay)timer to do what I think you want to do. You would give it a signal to the timer port and the inlet port at the same time (From the same signal). The signal would immediately pass th

    #21988
    admin
    Participant

    You can get both normally open and normally closed timers from KV Ltd.www.kvglobal.com

    #21989
    admin
    Participant

    With the products I am familiar with, you can use a 2/2 normally closed valve with a time in/out sequence adaptor. You would have air to the inlet of the valve. When you provided the pilot signal, the time in adaptor would delay for the preset t

Viewing 3 posts - 1 through 3 (of 3 total)